olddawgsrule
Advanced Member


USA
1434 Posts

Posted - May 21 2016 :  08:14:55  Show Profile  Visit olddawgsrule's Homepage Send olddawgsrule a Private Message  Reply with Quote
That time of year again to do the full inspection and clean/replace any connections, check water and give them a run on the SSG.

First how often do 'you' do this?

Second: I always get one battery that the terminals seem to corrode more.
Sign of the weakest battery?

Old in age, not in mind, so
'Teach me something new'!

Google AdSense

USA
Mountain View


49er
Administrator



USA
4426 Posts

Posted - May 23 2016 :  20:19:18  Show Profile Send 49er a Private Message  Reply with Quote
Water every 3 months
you have one or more cells that need the SSG

Doug
The sky is not the limit...There are footprints on the MOON.
Your only as DUMB as where your standing.
No matter where you go there you are.
You must be logged in to see this link.
SKYPE doug.bennett49er
Go to Top of Page

olddawgsrule
Advanced Member



USA
1434 Posts

Posted - May 25 2016 :  17:19:39  Show Profile  Visit olddawgsrule's Homepage Send olddawgsrule a Private Message  Reply with Quote
1) Check water every 3 months

Old in age, not in mind, so
'Teach me something new'!

Go to Top of Page

olddawgsrule
Advanced Member



USA
1434 Posts

Posted - May 25 2016 :  17:23:47  Show Profile  Visit olddawgsrule's Homepage Send olddawgsrule a Private Message  Reply with Quote
I'm going to list these as we go.
See if 'we' can build a good check list.

So, if I see corrosion building on the terminal, it will be a sign of running the SSG to revive that battery.
Correct?

How often do you run the SSG on the bank?
Even if it doesn't show the sign?
Should we or wait?




Old in age, not in mind, so
'Teach me something new'!

Go to Top of Page

49er
Administrator



USA
4426 Posts

Posted - May 25 2016 :  20:09:47  Show Profile Send 49er a Private Message  Reply with Quote
I use vasline on all terminals. End of problem check every year and apply where needed.
Voltage of eack battery in a bank should be with in .1 volt of each other at rest for 8 hrs NO USE
another way is under a load should be the same voltage, lowest is probly the one that needs help??? if all were the same at start if used anything is good.

Doug
The sky is not the limit...There are footprints on the MOON.
Your only as DUMB as where your standing.
No matter where you go there you are.
You must be logged in to see this link.
SKYPE doug.bennett49er
Go to Top of Page

olddawgsrule
Advanced Member



USA
1434 Posts

Posted - May 26 2016 :  17:55:12  Show Profile  Visit olddawgsrule's Homepage Send olddawgsrule a Private Message  Reply with Quote
Thank you!
I will add.


Old in age, not in mind, so
'Teach me something new'!

Go to Top of Page

olddawgsrule
Advanced Member



USA
1434 Posts

Posted - May 26 2016 :  17:59:31  Show Profile  Visit olddawgsrule's Homepage Send olddawgsrule a Private Message  Reply with Quote
Connectors between batteries.

I use the basic battery connectors and connect with 10g wire.
Should I be using something better?

Old in age, not in mind, so
'Teach me something new'!

Go to Top of Page

49er
Administrator



USA
4426 Posts

Posted - May 26 2016 :  19:38:32  Show Profile Send 49er a Private Message  Reply with Quote
How many amps max??

Doug
The sky is not the limit...There are footprints on the MOON.
Your only as DUMB as where your standing.
No matter where you go there you are.
You must be logged in to see this link.
SKYPE doug.bennett49er
Go to Top of Page

olddawgsrule
Advanced Member



USA
1434 Posts

Posted - May 27 2016 :  07:11:09  Show Profile  Visit olddawgsrule's Homepage Send olddawgsrule a Private Message  Reply with Quote
Battery or usage?

Batteries are Werker 205ah, chart rates them at 10a (C20) and have 2 good ones right now.

Since I only run lighting & and charges right now off them, I'm drawing about 1.5 - 2amps

I found the rating on the batteries to be optimistic.
Never could get tooling to run for any period of time.
Maybe I just haven't understood completely, but I now believe watts is watts.
Meaning, if my battery can create 120watts (12v x 10a), then converting to AC power I still only have 120watts. Now it's 1a of power (120w / 120v).
This thought falls inline with I saw for duration of the tooling.
(Tooling meaning, skill saw, table saw, drill press, sanders, etc)




Old in age, not in mind, so
'Teach me something new'!

Go to Top of Page

49er
Administrator



USA
4426 Posts

Posted - May 27 2016 :  10:44:45  Show Profile Send 49er a Private Message  Reply with Quote
Battery or usage is same, so your 10ga is good

Doug
The sky is not the limit...There are footprints on the MOON.
Your only as DUMB as where your standing.
No matter where you go there you are.
You must be logged in to see this link.
SKYPE doug.bennett49er
Go to Top of Page
  Previous Topic Topic Next Topic  
 New Topic  Reply to Topic
 Printer Friendly